PowerFlex4 Fault
yaofalin
Jul 2009
guangdong
F12 HW OverCurrent(The drive output current has exceeded the hardware current limit)
Check programming. Check for excess load, improper A084 [Boost
Select] setting, DC brake volts set too high or other causes of excess current.
I follow the Manual but the inverter still display fault.
d004 [Output Voltage] is higher about 5 Volts than the other inverters in the same environment.
Who can tell me why? Thanks!
What is the rated current of the drive output and what is the rated current of your motor? Is your motor bound up? Is it wired the same as the other motors (480v vs 240v)? Is there any phase to phase shorts in the motor windings?
yao, are you saying that the drive goes to F12 fault as soon as you power up. Even without starting the motor?
If so, the drive is damaged and needs to be replaced.
With the PF4, it has been my experience with that fault that there is a short in the drive output section, or the wiring or motor. For some reason, that fault will usually occur before a phase to phase or phase to ground fault is triggered.
If the drive is configured to run on power up, then the problem is likely in the motor or wiring between the drive and motor.
Disconnect the motor leads from the drive and then power it up. If you get the fault, replace the drive. While the leads are disconnected, test the motor circuit with a megger. I expect that even if the drive has failed, that there is a fault in the wiring/motor which caused it.
Quick question on the Powereflex 4 probably pertains to most drives. Does setting the stop command to "coast" eliminate the deceleration setting...
1,708
Getting back into this after a few years, was drewcrew6 back then. Can the pv talk directly to the powerflex, ability to start stop jog drive...
2,300
I'm new to the forum and have limited knowledge of PLCs and FReqDrives. I'm the only maint man where I work and need some info please. I have a...
17
4,994
Hey all. I just wanted to ask a quick drive question. I am trying to commision an old panel that came from another plant. It has many sets of...
1,559
Hi, I need to do Modbus communication between PLC(L73S Controller) and Powerflex 4 Drives. Does anyone tried this before? Thanks, Vinod