Powerflex70 speed does not follow 4-20ma signal
xinjiang
Mar 2010
Calgary
We are using powerflex70. But when analog current input is 4mA, drive para 16 is 6.8mA. When current is 12mA, it is 20mA. I checked all the config, it seems nothing is wrong. Analog input hi is set at 20mA and analog input lo is 4mA. Can anyone tell me why?
I am fairly new at this but it looks like you have your analog scaling off. Make sure it is set to the default of Configuration 1. Looks like you may be closer to Config 3.
Look under Analog Inputs 2-12 to 2-14 in the manual I have.
I infer from your reference to Parameter 16 that you are using Analog Input 1 on Terminals 16 & 17. Try using Analog Input 2 on Terminals 20 & 21. Make sure you change your Speed Command Source in Parameter 90, and the Scaling in Parameters 91, 92, 325, and 326 for your application. You can monitor the Input Current with Parameter 17.
Stu.....
The results you are getting are linear which has me thinking you may be introducing an error into your readings.
So are you able to measure the voltage across the drive input terminals, and read the current reading at para 16 at the same time, then apply ohms law to find the resistor value inside the drive.
Or post your readings
Voltage is measured in parallel with the input terminals.
Current in mA is measured in series with one of the input terminal leads.
I applied 4mA and para.16 is reading 5.554mA. I measured voltage across terminal 16 and 17, it is 0.557V. Still have no idea why.
Hey folks. Quick question about direction control on a PF70. The control is all over the connection on the 20-COMM-E. Start, Stop, Speed...
2,115
I need to add a couple of older PF70 drives to an application using PlantPAX, the 750 series have a fault list code in the library, but not the...
1,623
Hi, We have a Allen Bradley, Powerflex70 series A drive. We would like to use it as a test bench and programming station for communication...
1,592
I have an issue with a Powerflex70 drive communicating with a PLC5. The drive is setup as 1/2 rack and is communicating over remote I/O. It is...
1,831
hi we have a controlNet network with a PLC 5555 and several PowerFlex70 that are networked via COM C network adapters. Recently one of the...
1,261