361
Hi guys
I need to control a PF700 using CompactLogix(1769-L32E), 1769-SDN and 20-Comm Adapter. my question is how to configure the Logic Command Word and Status Word, what is the address for them in the PLC?
Hi guys
That will depend on where you map them in the SDN Scanner. You will need RSNetworx for DeviceNet to set it all up. Appendix D of the 20-COMM-D Manual has the Command and Status Word Definitions.