powerflex_10 MODBUS
ggchavhan
Nov 2006
pune
135
hi
I want to control Powerflex 10 by SLC 5/03 but I stuck, as SLC supports Serial port and PFx supports MODBUS. I wii ever grateful if anybody give idea about it and commu. procedure
Gajanan
If the Powerflex motor drive does not have a common communications protocol with the PLC, then you have to do it the long way: Use a PLC analog output to set the speed of the drive, and a PLC digital output to turn it on and off.
I presume you mean PowerFlex 40
There are several ways to have an SLC-5/03 controller perform Modbus Master functions.
One way is to use a DF1 -> Modbus RTU converter. A-B sells one specifically for the PowerFlex 4/40 drives, part number 22-SCM232. You can hook this up to the Channel 0 serial port of the SLC-5/03 and send MSG instructions to each drive.
Another method is to use a module from Prosoft Technology. The Prosoft MVI46-MCM module provides two ports that can be Modbus RTU Masters or Slaves.
If you have another communication network like DeviceNet connected to the SLC controller, there are DeviceNet/Modbus gateways and drive control interfaces for the PowerFlex 40 drives.
I am trying to control a Rockwell Powerflex 525 via Modbus RTU (RS485) using an ABB AC800M DCS controller, and am having some issues getting...
563
Setup: - Schneider Electric M340 PLC w/ NOE 100 Module installed - Allen Bradley PowerFlex 753 VFD w/ 20-COMM-M Modbus Adapter installed -...
4,621
how can i communicate with powerflex 400/40 through arduino with the help of modbus rtu/tcp. what is modbus register mapping of powerflex 400?
1,716
Hello I am a newbie so apologies in advance if I am not making sense or miss important information. I am trying to setup a PID Loop on a...
6,294
Hello, all I am hooked from an idec PLC to PF 400 Drive and need to read and write data via modbus rtu over rs485 I got it all hooked up correctly...
6,344