Problem Saving Channel Settings on AB 1771-IFE PLC5

hardaysknight

Lifetime Supporting Member
Join Date
Dec 2015
Location
Southeast USA
Posts
119
I'm having issues saving the individual channel settings on a 1771-IFE Analog card.



We recently swapped from 0-10v to 4-20ma transducers. I set the jumpers on the card, and set up the channel config in RSLogix5 and it works great, but any time the PLC is powered off/faulted/swapped to program mode, it goes right back to having a 0-10v channel configuration, throwing off our transducer readings.


This card is in a remote rack via controlnet

1771-IFE.png
 
Is this not right?


I'm gonna be honest with you, I have no idea what I'm doing.




EDIT: I figured it out. We aren't using a BTW to write the settings. We are using MOV instructions for each individual integer for the card configuration. No idea why.

1.png 2.png
 
Last edited:
You got it. I didn't notice you were using ControlNet. Local or expansion rack would have been block transfer.
 

Similar Topics

Ok, so yesterday I saw a new one (for me anyways). I'm writing a program that I've been working on for the last few weeks. I always make a habit...
Replies
9
Views
4,368
Hi, I have made some changes to a step 5 siemens program and decided to create a new file .I had the original file open(B2K1@@PX.INI) and went to...
Replies
6
Views
2,216
Hello, I am a plc engineer and I have a job to do in the NIGERIA 25000 TON GRAIN SILOS STORAGE CONTROL PANEL. A problem where the panel is not...
Replies
1
Views
148
The project on the operator workstation keeps disconnecting, even though I have an installation server and operating station set up through...
Replies
0
Views
64
I have a problem, I'm running an AE Licence Manager on a Windows 2016 Server, and my Window Maker is on another separate Windows 2016 Server. My...
Replies
0
Views
94
Back
Top Bottom