profibus
teh
Supporting Member
Nov 2002
140
Hi Friends,
Have anybody faces this problem before? the reading of scada(citect)
showing -negative value while the setting ranging is 0 ~ 200 deg c ( 0 ~ 27648 ). PlC i am using S7 300. The - negetive value appear not very frequence, several times per day, and funny thing is only occur to my temperature analog signal but not level, pressure signal.
Is that because of i am using s7 profibus for communication?
i dunno this kind of system is suitable for communication or not.
Are you sure the reading isn't coming from the actual device or is it truly a profi-bus communications problem?
I never dealt with any of that but it may help someone else answer.
Drewcrew6
I faced similar type of problem recently.We had Siemens PLC and MMI on profibus.Analog inputs are all showing negative or zero value. But I found this is due to combination of problem - 1.position sensor problem 2. Voltage drop problem. Is it possible you to check the voltages ?
Hello !
Have you checked the temperaturegauge ? If you use thermocouples you can get that kind of problems ! What about the kompensation "resistor"?
If you have pt 100 maybe it's broken ?
That problem should have nothing to do with profibus communication, it's just easy to always blame the fieldbus..
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
195
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
90
I am trying to implement a profibus network and am a newbie in the automation and communication industry. what are the components required for the...
112
Hi, I am using TIA Portal V18. I have imported a (v5.7) SIMATIC manager project via device proxy. I have created a HMI project (TP700) in TIA...
325
Hi Folks, I am new to the S7-300 and the whole Profibus communication. And I just wonder that can you connect a S7-300 module to a Beckhoff Bus...
321