Profibus

ABDELAAL

Member
Join Date
Dec 2007
Location
ALEX.
Posts
32
HI EVERYBODY,

I've a plc siemens S7-300 and I want to interface a profibus based flow meter do any one have a solution for this ?
 
In what way do you mean "do any one have a solution for this"?

You will need the GSD file for the flow meter; ask the supplier for it.
 
I mean that i need a manual for fb for cofiguration of the profi. i think first time it wasn't clear
 
You will need the manual for the flow meter and also the gsd file.
This will tell you what data areas can be used and what bytes or words within the data area are for what.
With this information you can write your code for the PLC
 