Protection for PLC output card relays
AB2005
Nov 2006
Lahore
320
Dear All,
I want to connect MOVs (Mattel Oxide Varistor)with parallel of coil of each relay (220VAC) which are energizing through PLC out put Relay card for providing protection to the output card relays contacts against high voltage spikes occur when relays de-energize. But I haven’t experienced ever before.
Please help me for selecting the proper MOV.
AB2005,
How big is the coil in question? You need to select your MOV based on the amount of energy expected to be produced by the collapsing coil, measured in Joules, (watt seconds). There are maybe a dozen specifications for MOVs. Your main concerns for arc suppression is the working voltage and the capacity for energy absorption/crossover.
The RC snubber is a better way to go for an inductive coil. The RC snubber will supress transients created when the coil de-energizes. A MOV does not help supress a transient. It lets the transient thru when the transient energy is greater than the energy rating of the MOV - a MOV is rated in Joules. MOVs are frequently used across solid state output devices such as SCRs and Triacs to protect the semiconductor switch by letting high energy transients go around the semiconductor switch.
Agreed. MOV's won't supress the arc across the relay points. A snubber will.
I have a question about overload protection for I/O modules 120v and 24v. I was curious to see is there any reason to protect a input considering...
3,359
Hi group! Repeatedly found answers to some questions in the PLC's programming world, now I decided to ask the question directly) Now I am...
22
4,295
Could someone explain how it is possible to use the Siemens S7 1200 internal fault contact bit M100.0 to operate a digital output signal which...
1,272
2,551
Good evening everyone! This is my first post here, after extensive searching on the net I couldn't find an answer to my question so I thought I...
3,490