Pump Flow calculation from level
sdb83065
Jul 2003
Strafford, NH
22
Has any one used a good volumetric flow algorithm utilizing level and pump run indication? I know some ultrasonic level transducers will calculate volumetric flow pumped but I need to use the existing pressure level transmitter. I could use a standard volume formula to calculate the amount pumped but that does not take into acount the changes that occur with the influent while the system is pumping. This is for a lift station with no influent or effluent flow meters and of course the influent is always changing. Any assistance would be greatly appreciated!
By the way this is a great site! I wish I had this resource available when I started in this crazy field!
You've identified the problem exactly. I am going to assume this is a wet well level with intermittent pumping.
The first step is to calculate the volume pumped from the level change during the pump run cycle - area times depth change. You can get the level in feet from your "level" pressure transmitter since 1 psi = 27.7" H2O.
The tricky part is to get the additional flow rate from inflw during the pump run cycle. The typical way to do this is to measure the time and level change to go from the pump off to the next pump on. This identifies the flow rate into the wet well. You have to assume that this is the same during the pump cycle, and add it to the first flow rate.
Hey everyone, I was on a customer's site on friday where they have a large bioreactor that they bought secondhand from a previous user. System is...
22
4,500
Hi The pump smart PS220 VFD has the ability to estimate pump flow based of pump characteristics and measured motor data. The calculations...
3,760
Hi, Just got a specification from a customer that said: "The outlet flow to be controlled by: - A combined flow rate/outlet pressure for all...
4,076
Dear, We have a Variable speed pump located in an underground pit, the purpose is to perform the following 1- When the level is high, the pump...
3,648
Hello, I take part in commissioning of process station with lobe pump. Speed of the pump is controlled by PowerFlex 525. A customer requirement...
5,556