PV 550 error 208
Here is the file that was causing the issue. The only change that we made was removing the jumper bit from ladder 2 rung 0000. Maybe some one could let me know why this could cause the 615 error on the PV. thanks
Well the error was gone for a day and now it is back. Everything is working fine we are just keep getting a random 615 error on the PV. The next thing I am going to try is to pull a new com cable from PLC to PV and see if it is just EMF that is causing issues (the cable installed now is sheilded but it is run with all of the control and motor cabling) I will update you when I get that done.
Update on the reason for the 615 issue? I personally am having this issue, but had to replace the PV to PLC wires on my system because they keep "burning out", according to my end user. So we're at the 3rd set of wires. Any suggestions as to why I may be getting error 615?
Tell us what PLC you have and the cable you are using. Also the complete catalog number of your PV.
615 Duplicate node
address
Comm Status More than one node was assigned the
same address.
Verify all device nodes.
Hello, I was trying to create new module in I/O Configuration and I get the "Fatal Application Error" Below is my plc setup if I need to try...
1,514
Hi, Has anyone had this problem: - I send a speed reference to my ABB ACS550 Drive via Modbus TCP to it's register via an INT. However when I...
1,040
Good morning, We have an older HMI, PV 550, 2711-B5A9. Just attempted to download an application to it and after the download was comlete we...
2,359
Good evening everyone. I am working with the follow equipment Controllogix 1756-L55A/M13/A ControlNet 1756-CNB/D Channel A Panelview 2711-K5A2...
1,935
Hi Guys, Has anyone ever displayed error codes from a cip drive to a HMI? I contacted Rockwell and they gave me a sample bit of code but it will...
1,797