Question about star-delta control circuit diagram

Wye delta

K1T ( n.c.) is in wrong location. It should be on 2nd rung to open k1 resulting in k3 being energized by k1 interlock . Basically transition from wye to delta connection.
 
K1T ( n.c.) is in wrong location. It should be on 2nd rung to open k1 resulting in k3 being energized by k1 interlock . Basically transition from wye to delta connection.
welcome to the site
Can you please check the date of the last post

2009 is very old
 
Hi Shilpesh
From your circuit diagram,K1 is for STAR connection.For Star delta Starter,The first sequence after you press ON push button is K1 MUST energize first before K2.Why? because if K2 energize first before K1 it can cause the spark and can damage the contactor. The Key point for star connection is to start the motor in 240 Volt to reduce high in rush ampere and build a torque..after a motor achieve 80% running..it switch to Delta.It mean the motor running with full capacity ( 415 volt )..For more detail,please read some post about star delta starter below :-

http://www.electricneutron.com/electric-motor/star-delta-motor-connection/
http://www.electricneutron.com/motor-control/star-delta-starter/
 
Hi Shilpesh
From your circuit diagram,K1 is for STAR connection.For Star delta Starter,The first sequence after you press ON push button is K1 MUST energize first before K2.Why? because if K2 energize first before K1 it can cause the spark and can damage the contactor. The Key point for star connection is to start the motor in 240 Volt to reduce high in rush ampere and build a torque..after a motor achieve 80% running..it switch to Delta.It mean the motor running with full capacity ( 415 volt )..For more detail,please read some post about star delta starter below :-

http://www.electricneutron.com/electric-motor/star-delta-motor-connection/
http://www.electricneutron.com/motor-control/star-delta-starter/

welcome to the site
It is great to see new input from new members.
but
please check the original post date
this is from 2007 (5 years old);)
 

Similar Topics

Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,666
Hello all, I have a servo turning a small table on a machine I'm programming. I found that after a day the home position was getting off by a...
Replies
1
Views
54
Hi, I just upgraded just restored a ftview hmi data and the trend file have question marks with no lines in the graph. How do i fix this?
Replies
0
Views
16
Hey all, simple question. Once I create a Macro in my Factory Talk Project, do I need to trigger the macro to run somehow? Or are all macros...
Replies
8
Views
114
I recently uploaded an aplication from a Panel View, created a new screen and now that I've downloaded it to the Panel View, all the texts have...
Replies
9
Views
174
Back
Top Bottom