Rated motor Voltage setting on Siemens Micromaster VFD
killer
May 2008
York Haven, PA
106
I'm trying to decipher the manual on the Siemens Simovert Micromaster drive. I think this is the case, but I'd like someone else's opinion who has more experience.
Can I use the drive rated for input voltage of 575vac 3-phase, and then set it to run a motor rated for only a nameplate line voltage of 440VAC?
Using drive 6SE7014-5FB61.
Parameter P101 seems to suggest this but doesn't really specify.
Is it considered too obvious to actually specify? The drive I usually use (non Siemens) doesn't allow this.
this's no a micromaster drive, is simovert masterdrive :>
yes you are right, you can use it with 440VAC motor by setting P101=440VAC, and you must have a supply voltage greater than 440VAC. and you have to specified it in P071 - Input unit line voltage
Thanks !!! That makes my life easy.
I'm new to this Siemens stuff and sometimes the manuals just don't make sense to me. (when I can actually find them)
A big word of caution on this, however. With an input voltage of 575VAC, the drive output pulses will be around 815V high instead of the usual 660V when the input is 480VAC.
These higher voltage pulses can be limited to the PWM equivalent of 480VAC but the pulse height will still be 815V. This places additional stress on the motor insulation and I would expect early motor failure as a result.
Placing a motor lead reactor between the drive and the motor will protect the motor somewhat and cause the reactor to deal with the pulses. I would definitely do this to protect the motor.
I got it to work. The drive monitor software was a big help.
No adverse effects noticed on the motor.
Thanks for all the advice.
HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
677
Hi All I am hoping there is some here on the list with the "Black Belt" in JVL servo motors :) I have a MAC3000 motor controlled via Ethernet IP...
1,771
I have an application with just one servo positioning axis on a jackscrew, and there is very little room for an electrical enclosure. In...
1,090
Hello All, I just finished programming some solenoid valves. I have to now program some Motor Operated Valves. The Controllogix PLC has 2 120VAC...
5,564
Hello to all We have a several small inverters that are under rated, 1.5 FLA on the name plate on the motor, it has a 10 to 1 ratio gearbox...
4,734