Reading string variables in iFix from controllogix
LMDAVE
Oct 2006
New Orleans, LA
50
I recently converted a PLC-5 program to Controllogix and using iFix as the graphic interface. I seem to have trouble reading a string and displaying it on the screen.
The string is ST48:0 from PLC 5. I mapped the ST file address to PLC5
in iFIX, the datalink i have
ifix.node.TAGNAME.a_cv
where TAGNAME is reading ST48:0.TEXT through ABR to Controllogix
it doesn't seem to poll the data with ABR from controllogix to update the database. Everything else is fine, integers, bits, etc..
Hello,
I believe I ran into this same problem. In your iFix Database - instead of defining your tag I/O address to: ST48:0.TEXT try ST48:0.Data
Example from one of my applications that uses the IGS:
iFix Database Manager:
Tagname = UPLD_BRASS_TAG type TX
I/O Address = CHANNEL1.TB_OVEN.Prgm_MainProgram.SC_Brass_Tag.Data
Control Logix:
Tagname = SC_Brass_Tag (string)
Additionally - You may have issues with using a ":" for a tagname. I would recommend (Control Logix) renaming the tag ST48_00 or something to that order. I'm Not sure if it makes a difference in this case, or not.
The problem with me converting a PLC-5 program in control logix and using the ABR driver, I have to map controllogix to PLC5 addresses. ABR doesn't like or let me use ".data" so the mapping doesn't seem to account for ".text" to ".data".
So I may have to use a OPC command in the database to read directly from contrologix. Only thing, I don't know the correct nomenclature to do that. I'm using RSLinx Classic
A Couple of questions:
1) What version of iFix & ABR driver are you using?
2) On the ABR driver - is there a datablock set up to read the string address?
3) Have you considered using IGS instead of RSLinx & ABR?
Hi, How does one go about reading a string over modbus? I can convert the string to 16 bit integers without a problem. How does the Modbus...
2,903
I am trying to read a string from a remote compact logix to another compact logix. I have the msg instruction is setup but it keeps coming up in...
2,680
I have an existing Ifix PIC that is reading a SQL table when an down time timer times out. The operator clicks on the popup, choose a button with...
3,353
This is the configuration: - MP277 10 Touch, configured with WinCC flexible 2008 SP1 HF2 - CPU S7-315 2DP - If I write in the DB of PLC "ABCDEFGH"...
2,164
I'm attempting to read some strings from a S7 300 PLC over ethernet. I'm using a IBH S7 Link mpi to ethernet converter and then use IBH OPC server...
6,433