Recommend PLC to bridge DH485 and Ethernet networks
sanger
Nov 2005
Toronto
172
I need to consolidate data from PLC's on two DH485 networks and serve them to a SCADA system over Ethernet for access using a Kepware OPC server. The data needs to be re-organized before presenting to the SCADA system so a simple Ethernet to DH485 gateway will not do.
The PLC will have no other purpose than acting as a data concentrator and will have no hardwired I/O. A ControlLogix rack with a 1756-DH485 module would be an easy solution but is way overkill for what we are trying do. Any recommendations on Rockwell's lower-end processors that support multiple DH485 networks. Rockwell's offerings in the mid/low end have grown so much in recent years I can't keep up with the capabilities of each line. I'm not interested in considering the Micro800 line. Haven't had good experiences with them.
I think MicroLogix 1400 is the way to go.
It has Ethernet as well as two serial ports, each of which can be configured for DH485.
Channel 0 is the round port; you can connect it to a non-isolated RS485 network with a 1763-NC01 breakout box, or use a 1761-NET-AIC if you want good isolation.
Channel 2 is the DB9 RS-232 port; use a 1761-NET-AIC to connect it to a DH485 network.
I'm on the hunt for for a "Balance of Plant" PLC (or alternative) that is capable of exchanging (sending and receiving) a small number of bit...
2,184
Hi All, I'm looking for a PLC and HMI for a small brewery to monitor fermenter temperatures and adjust setpoints. The part I'm struggling with is...
3,580
We got 23 Batch mixer that can heat (with water, steam or oil) or be put in Cooling ( Water or Oil) and all the heat/cooling work with Pneumatic...
2,933
Hello all, love the forum. So, I'm not really a PLC programmer... I'm an EE with lots of experience with FPGAs and programming, but...
6,948
I hope someone will recommend a small (read inexpensive ) PLC or relay of some sort. It needs to have 4 24vdc digital outputs 1 4-20 MA input 1...
2,213