i just search a sample code typed with rslogix 5000 with the necessary step to configure a redundant system using controllogix controller.
thanks.
There are two necessary manuals you should read and understand for the use of ControlLogix Redundancy.
The first is the ControlLogix Redundancy User Manual, which covers the basic principles of ControlLogix Redundancy. There is also a newer Enhanced Redundancy User Manual that includes the newest modules and functionality.
The second is the Release Notes publication for the specific version of Redundancy you are going to use. The modern 1756-RM redundancy module requires different network and controller modules than the older 1756-SRM module, and the firmware and hardware versions described in the Release Notes must be followed exactly.
All RA Publications can be downloaded from the Rockwell Automation Literature Library. Use the Search function with the Keyword "ControlLogix Redundancy" to find the publications related to Redundancy.
http://http://literature.rockwellautomation.com
Examples:
ControlLogix Enhanced Redundancy User Manual, Publication 1756-UM535B
ControlLogix Enhanced Redundancy Release Notes version 19.81, Publication 1756-RN650D
Hi Experts, I need to test if a ControlLogix redundancy system will switchover when the Primary chassis has a major fault occurred. I followed...
1,862
Hi all. i'm implementing a contrologix redundant system, each chassis of the redundant pair have two 1756-EN2TR for a DLR network. The...
5,566
Hi Everybody, I have a question regarding ControlNet in ControlLogix redundant configuration. I have two ControlLogix PLCs working in a redundant...
5,757
I'm developing a project for a ControlLogix Redundancy System, using 2 chassis with the 1757-SRM modules. The redundant processors control some...
6,658
Hi, I am getting an error in hmi server redundancy. I have SERVER A,SERVER B,SERVER D. total 3 servers Server A and Server B are redundant hmi...
3,847