Redundancy
There are many levels, or types, of redundancy.
Some Redundant Systems go as far as having multiple PLC's and multiple field devices. The more critical the situation, the greater the need for redundancy. The Space Shuttle has multiple redundant Systems.
You asked for a "simple" example. An E-Stop typically has 1-contact dedicated to the power circuit (it might also have another contact dedicated to an indicator for that E-Stop).
You can increase the reliability*** of the E-Stop Function even if the contact is fused closed. You do this by adding more contacts onto the E-Stop. If you have three contacts, wired in series, instead of one, the E-Stop Function becomes more reliable.
*** This really only increases the reliablility of the contacts and therefore the Function... HOWEVER... there is still a chance that the E-Stop itself can malfunction. In that case, having 20 contacts on the E-Stop wouldn't make a difference!
You only have to go so far before your redundancy starts to become redundant!
Terry gave a good explanation.
redundancy:Electronics. Duplication or repetition of elements in electronic equipment to provide alternative functional channels in case of failure
A simple example is when using dual contactors on a system in series, the controller monitors the auxillary contacts on the contactors. IF for any reason either contactor doesnt close OR open (when they should) then the system will go into alarm mode. The use of 2 contactors and auxillary contacts is redundant.
I looked up redundant in the dictionary
I looked up redundant in the dictionary. It told me to see redundant. [Robin Williams]
Redundant system.
At many locations I would install a PLC to take place of a relay logic system. Most all cases the relay logic system had became in bad repair and something had to be done and some inovative young tech had convinced the upper management to install a PLC. Not only did I install a PLC I had to recondition the relay logic system for REDUNDANCY, they didn't trust the PLC, they insisted on the redundant system.
Roger
Redundently Redundent
When I worked an a famous Nuclear power plant all of our critical systems had a 100% identical backup system. A and B. Each of these systems had two emergency safeguard activation systems (ESAS) monitoring them. System A had ESAS A&C monitoring it. System B had ESAS B&D monitoring it. Then the ESAS system had a two out of three logic scheme monitoring it. All of this was designed and built before the advent of PLC's.
All system there also used what I would call passive redundancy. every wire, relay, bolt, etc was de-rated. #10 wire could be loaded to 15A, etc.
So I guess the question of how much redundancy do I need depends on how ugly thing could get if the primary system fails.
Was that TMI?
In that case the redundant human controllers failed.
We use rdundancy for PLC's as well, 2 PLC's with the same program if one crash the other take the relay!!
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
99
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
211
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
89
Guys, please help me with this urgently. We have Logic 5575 installed in hot n standby setup. For some reason, the primary now cannot sync with...
386
Hi Guys, Is it okay to have Redundancy ControlLogix Processor IP address set to DHCP? I had Static IP address on it but removed it via RSLinx...
243