Relay Output Of a VFD
sharks
Feb 2008
Dubai
33
Hi all,
What is the use of relay output in the VFD. How it will work and what about the connection. Please brief me. I am using both LG and Altivar products. Till yet I did not use the relay output. But I want to know about it.
sharks said:
Hi all,
GENERICALLY You can do with it as you would with any switch subject to the same limitations AND if it is solid state you may need to watch out for PNP vs NPN ie sink or source.
What we just did is use the ralay to drive a contactor for an auger motor on a large grinder.
Read your VFD manual - it should tell you how to hook it up and what limitations there may be.
Dan Bentler
On most vsd's you can assign functions to the realy outputs. Example you assign a fault to a relay and the contact will close or open (n/o and n/c) when the drive goes into a fault condition.
You can use it for a run feedback. when it reaches a certain speed......... The list goes on. Just check your drive manual
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
112
I’ve got some devices that are triggered by shorting pins to common. There is 24 volts on each pin and right now I am using a relay output card...
2,586
I have a Automation Direct Click Plus that you can buy option CPU slot modules for input/outputs. The slot modules have the options of sinking...
2,840
Troubleshooting a Eaton Easy719-AC-RCX. Have three digital inputs and one relay output. PLC input power 120VAC. Each digital input has a 120VAC...
2,001
Hi all, A client is asking if I can move a motion sensor from an existing alarm dialer to a PLC discrete input. Looking up the datasheet, it...
2,298