Remote I/O

ashumate

Member
Join Date
Oct 2007
Location
Evansville,IN
Posts
1
Im am designing a system containing a compactlogix controller with controlnet communication. I have some 24V I/O (8 inputs and 8 outputs) 1000 meters (3280 feet) away from the controller. I am looking for some recommendations on how to communicate with the I/O. The communication doesnt have to be fast, the I/O is mostly pushbuttons and lights. Should I go with controlnet? I might have to get a repeater (control net on coax is only good for 1000 meters). Should I go with remote I/O (I would need to purchase a card )? I am also not sure about the I/O module choice either. Point I/O or Flex I/O? any help is appreciated. thanks
 
Well is there a pupose you are using a Controlnet processor? If you use a processor with Ethernet/IP you could run fiber out to your remote station. There is no AB "Remote I/O" for compactlogix. Running coax that far will be more expensive than a fiber run i would imagine.
 
For I/O, and since you already have controlnet, definitely cast my vote for that over ethernet.

Use ethernet for HMI, programming terminal, and any peer to peer stuff so you don't have to buy a PC card for controlnet.

Get the ControlNet Media planning guide from ab.com too...There will be more planning and work in the media installation versus the ole blue hose RIO, but it's a super fast, reilable network in my limited experience. Easy to diagnose and keep downtime to a minimum.

The only failures I have seen were both acoompanied by flashing red LEDs on the faulty segment pointing to a failure of a passive tap, and the other was a "failed" repeater (not a fiber optic one).

It is very simple to dial the node number on any c-net network device with a screwdriver and plug and play...much more maintenance tech friendly IMHO. Both times the on-shift tech got it going without having to call in engineering support.

1 more vote for C-Net
Paul

EDIT: If you spring for the PC card for controlnet, you can plug into your remote rack and have ethernet speed to program your CPU 3280 feet away. This was very handy on our machines, to be able to park my PC right by the I/O I was working on and debug, and fine tune speed controls, etc...
 
Last edited:

Similar Topics

Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
54
Hello, Can anyone recommend an expandible IO module with OPC UA? I've deployed the Emerson RSTIO-OM module and it works great, but it has a...
Replies
0
Views
48
So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
Replies
8
Views
257
See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot...
Replies
7
Views
301
Hello Dear users, I am writing about a problem that has been bothering me for a few days, i.e. I am trying to establish remote access to the Allen...
Replies
0
Views
103
Back
Top Bottom