If you have any issues, connect the brown wire from the Ethernet cable to SG.
Thank you, i've made the cable but i'm still unable to start the motor. I use following devices:
HMI XBTGT 4330 7"
Programming software: VijeoDesigner 4.6.0.7613
Twido PLC TWDLCAE40DRF
Programming software: TwidoSuite 2.0
Altivar 71
Ethernet communication between HMI and PLC works fine, i can set the speed on HMI and correct value is displayed in animation table on PLC. I used following settings on Altivar:
Communication - Modbus Network:
Address: 2
Baudrate: 19200
Data bits: 8
Time between frames: 10
Command: Ref.channel 1: Modbus
Ch1 active
Profile Not separ.
System word %SW64 keeps returning (modbus) error code 8. I have NST message on Altivar with these settings; if I try to use I/O profile it says RDY but does not receive anything from PLC, or returns CRC 2. I've read manuals, checked wiring and tried pretty much everything I could think of, but no luck
HMI and Twido programs are included in attachment. I would be very grateful for any suggestion regarding this issue. Tyvm!