Rockwell controlnet Connection?

wilsonzhu

Member
Join Date
Jan 2008
Location
vancouver
Posts
278
Hi, I have a big project which has 6 17-slots Racks connected by Controlnet. How much the maxium scheduled Controlnet connection? If I use comm formt:Rack Optimization instead of input/output Data for DI/DO Cards, Will it save Connections? Thanks,
 
Yes, using Rack Optimisation will reduce the number of connections utilised.

Example : A 17-slot chassis full of Digital* I/O modules will require 16 connections. Using Rack-Optimisation reduces that to 1 connection.

* Analog I/O modules cannot be added to the Rack Optimisation method.

Disadvantages : None except that all digital I/O in the chassis has to run at the same RPI rate. If you do need an I/O module to run at a different rate, it can be added to the configuration so as not to use Rack Optimisation.
 
What's the maximum connections for Scheduled controlnet?
Yes, using Rack Optimisation will reduce the number of connections utilised.

Example : A 17-slot chassis full of Digital* I/O modules will require 16 connections. Using Rack-Optimisation reduces that to 1 connection.

* Analog I/O modules cannot be added to the Rack Optimisation method.

Disadvantages : None except that all digital I/O in the chassis has to run at the same RPI rate. If you do need an I/O module to run at a different rate, it can be added to the configuration so as not to use Rack Optimisation.
 
How to change Comm format, it's grey color, I can't change, Does it must delete and then add?

Yes, you must delete and put back in Rack-Optimised format.

The reason is that this changes the Module-Defined tags that are created, and any existing I/O references are aliased into the rack-optimised tags. This subject usually takes me an up to an hour to get across to most people.

Connection usage is limited by :-

a) The processor - 250 maximum
b) The comms module - the CN2 have twice the nunber of connections than the CNB, the specs will tell you how many each module will support.
 

Similar Topics

Hello all, I am an Industrial Electrician, and deal with a little bit of everything including PLC troubleshooting and programming. When I started...
Replies
3
Views
114
I am working on a large migration of the standard PID instruction to the PlantPAx P_PIDE. Has anyone done a migration like this before and have a...
Replies
0
Views
85
Hi all. What is the purpose of that block (MVM) when used with a 2#1111_1111_1111_1111 mask in that situation? I'm really hoping there is...
Replies
5
Views
153
Customer is adding an extension rack to an existing A22. They wired and powered it up, I configured the new cards in the PLC starting from slot 23...
Replies
4
Views
133
I have got an Rockwell PLC 1769-L36ERMS . I have assigned a IP address to it . But every-time I Reboot the PLC it looses Communication to my PC...
Replies
1
Views
101
Back
Top Bottom