Rockwell EN2T sending SNMP message?

mugged99

Member
Join Date
Feb 2015
Location
MI
Posts
22
I'm trying to figure out if it's possible for an EN2T card along with an L7x processor be used to send SNMP protocol messages? I'm pretty sure the card can receive SNMP queries but not sure if it can source them.

Basically I'm looking to retrieve data from a piece of hardware that is SNMP enabled (an SNMP agent) over Ethernet/IP using the PLC.

Any ideas?

Thank you
 
I'm trying to figure out if it's possible for an EN2T card along with an L7x processor be used to send SNMP protocol messages? I'm pretty sure the card can receive SNMP queries but not sure if it can source them.

Basically I'm looking to retrieve data from a piece of hardware that is SNMP enabled (an SNMP agent) over Ethernet/IP using the PLC.

Any ideas?

Thank you

In the S7 world, I've used a published SNMP library to change which wireless access point an AGV was looking for as it moved around. No reason I can think of shouldn't be possible in AB land.

The question is if there is an existing library, or if you have to build it from scratch with open socket messaging.
 
I'm trying to figure out if it's possible for an EN2T card along with an L7x processor be used to send SNMP protocol messages? I'm pretty sure the card can receive SNMP queries but not sure if it can source them.

Basically I'm looking to retrieve data from a piece of hardware that is SNMP enabled (an SNMP agent) over Ethernet/IP using the PLC.

Any ideas?

Thank you

Since Prosoft will sell you a dedicated card to do SNMP protocol, and to do the polling of the various 'layers' .. I'd guess that it's not easy to do.

A quick search of Knowlegdebase gave me tech notes on what the default Rockwell passwords are, how to change them, which products support SNMP. No info on how to source SNMP messages.

It may be possible ... I have not been successful in searching Knowledgebase in the past .. I may be using bad search terms
 
SNMP - Not so Simple?...

mugged99 said:
...I'm trying to figure out if it's possible for an EN2T card along with an L7x processor be used to send SNMP protocol messages?

First...

493224 - SNMP commands from a ControlLogix PAC
Access Level: TechConnect

So that's a Roger...and that information also now pertains to many more products besides the older 1756-EWEB...

470690 - Open Sockets Support in ControlLogix and CompactLogix
Access Level: TechConnect

...and some reference material and examples...

48879 - Summary of Logix Open Sockets Information
Access Level: TechConnect

Regards,
George
 
First...

493224 - SNMP commands from a ControlLogix PAC
Access Level: TechConnect

So that's a Roger...and that information also now pertains to many more products besides the older 1756-EWEB...

470690 - Open Sockets Support in ControlLogix and CompactLogix
Access Level: TechConnect

...and some reference material and examples...

48879 - Summary of Logix Open Sockets Information
Access Level: TechConnect

Regards,
George

Thanks Geospark. You are obviously much better at this searching thing than I am.

I am always amazed at what information I am not able to locate in Knowledgebase!
 

Similar Topics

Background for the question: A service man from a sub-supplier has made changes onsite to a Siemens PLC and HMI program. He has not made a backup...
Replies
6
Views
154
Hello all, I am an Industrial Electrician, and deal with a little bit of everything including PLC troubleshooting and programming. When I started...
Replies
3
Views
154
I am working on a large migration of the standard PID instruction to the PlantPAx P_PIDE. Has anyone done a migration like this before and have a...
Replies
1
Views
168
Hi all. What is the purpose of that block (MVM) when used with a 2#1111_1111_1111_1111 mask in that situation? I'm really hoping there is...
Replies
5
Views
172
Customer is adding an extension rack to an existing A22. They wired and powered it up, I configured the new cards in the PLC starting from slot 23...
Replies
4
Views
151
Back
Top Bottom