Rockwell - Generic Ethernet Module

mugged99

Member
Join Date
Feb 2015
Location
MI
Posts
22
So Rockwell PLCs have some generic ethernet module options available in the IO tree configuration. With the standard generic ethernet module, you can define any standard user-configurable device without needing the EDS file or extra software since Rockwell creates the "devicename:C" configuration tag in the controller tags. However, when I try to do the same with a generic ethernet safety module, there is no corresponding "devicename_safety:C" tag. Does this mean it's impossible to define a safety-user-configurable device? An EDS or extra software to do the device configuration is absolutely required? As an example, a safety IO block where the IO points can be configured in different ways. Thanks.
 
What version are you using? This v33 has a configuration instance available for the standard connection I/O - Images attached.

1.JPG 2.JPG
 
v32 but yes that 'C' tag is for the standard configuration assembly. If you put up a safety generic module instead of your standard&safety generic combo module, there wont be any 'C' tag.
 
What's the device you're trying to connect?

If the Configuration Assembly isn't handled in the standard tag scope, and the device is intended to be configured then you may need to use MSG instructions to Get/Set Attribute of Configuration Assembly separate to the I/O connection.
 
Last edited:

Similar Topics

Is it possible to add another AB Rockwell PLC to the network tree as a Generic Ethernet Module and use it as IO? Any idea where I would find...
Replies
9
Views
3,158
Hello all, I am an Industrial Electrician, and deal with a little bit of everything including PLC troubleshooting and programming. When I started...
Replies
3
Views
104
I am working on a large migration of the standard PID instruction to the PlantPAx P_PIDE. Has anyone done a migration like this before and have a...
Replies
0
Views
83
Hi all. What is the purpose of that block (MVM) when used with a 2#1111_1111_1111_1111 mask in that situation? I'm really hoping there is...
Replies
5
Views
151
Customer is adding an extension rack to an existing A22. They wired and powered it up, I configured the new cards in the PLC starting from slot 23...
Replies
4
Views
131
Back
Top Bottom