Rockwell Redundancy Error
Basit Jamil
Nov 2021
Lahore
Hi everyone... I'm not a AB expert.. I'm using L74 controller, Rm2 redenduncy module, EN2TR and EN2T module (on each chassis) on my control logix project and having 3 remote IO's rack on ring topology... I have use EN2TR for ring topology and EN2T for scada communication. The problem is my controllers are not synchronising on fibre optics... I have to connect both EN2T modules with one an other for controller's synchronisation. They are syncing over ethernet but not over optical... your help is appreciated
Thanks in advance
[FONT=&quot]Basit Jamil[/FONT]
[FONT=&quot]This is normal.[/FONT]
[FONT=&quot]The Redundant controllers will not go to SYNC if any of your Ethernet modules don’t have a valid connection. Once commissioned, loss of an Ethernet connection is a trigger for a processor swap. They are not syncing over the ethernet but it can be a backup.[/FONT]
Thank you for you response... but all my modules connections are fine... EN2T modules connected with the ethernet switches... when I connect both switches "SYNC" status comes... but when the both switches are not connected with each other I get disqualified status
Not sure if I'm understanding you correctly but BOTH the fiber (between RM2) and ethernet (between EN20--) need to be connect in order to sync.
With ControlLogix redundancy primary and secondary Ethernet modules must be able to see each other on the network, this is exactly what your are seeing.
Fiber cable between two RM2 modules is used to cross load your program and data.
Is anyone here using the latest version of Rockwell FactoryTalk View (RSView) SE in a redundant server configuration? How well does the...
3,771
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
170
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
129
Hello, recently I saw a graphic from any Rockwell App, I cant identify which one is. Attached a SS. Its used to see dashboard from datapoints and...
127
I'm working with a project that contains some routines in ST but mostly in ladder. Am I correct in assuming this 'rung': DB1001DO._01AV55_OPEN :=...
114