RS-232 Communication with Polyscience Chiller
I figured it out! It involved using the AWA and ARl instructions rather than the ARD and AWT instruction. The only quesiton is: why couldn't I use the ARD or AWT instructions? I used the proper CR termination?
The AWA and ARL commands Write and Read only a specifed number of characters from or to the RS232 buffer, with the number entered in the instruction box. I would guess that in your earlier tries, you were writing more characters than the two-character+CR chiller commands, and trying to read the entire buffer instead of the 7-character response from the chiller. That is why early in this thread, I asked you WHAT was being written from string ST9:0
What is in the 12 characters of ST9:0?
I knew that if ST9:0 conatained more characters than the specificed chiller command line, you would get zilch in return.
You can use the other earlier commands, if you make sure you are writing and reading the number of characters with proper CR, as used by the chiller program.
I was messing around using the hex conversion for the RS[CR] command. I changed it back to RS[CR] and now reads 6 characters. I also tried it without the brackets or RSCR.
This was my response to the question regarding ST9:0 in other words the 12 characters was me trying a hex conversion which of course didn't work. I did try it with RSCR and it did not reply.
I had my number of characters set to 0 which, according to the instructions means it should read what ever is in the buffer. Or is this not correct?
Yes, but the PLC RS232 buffer can contain many more characters, everything that has been sent after it was last cleared. If you use the commands that read or write the entire buffer, then you have to control what is in the buffer, not just in one line or in a string up to the next CR character. To control what is in the buffer, you have to "handshake" with it using one of the control bits, such as R6:0/DN or similar.
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
2,629
Hi friends, I have a problem. I want to read ASCII data over rs232 standard port. How can I do the reading process? FATEK FBs-CB25 -> port1...
769
MELSEC A RS422 (25pin) <> iQR C24 Serial RS232 (9pin) - Simple PLC Communication Communication from a MELSEC-A Series CPU (RS-422 – DB 25 Pin)...
1,070
Good morning everyone, This is my first post here. I am beginning my journey on PLC programming and still a really newbie, I want to write a...
1,284
Hi, I want to communicate slc5/03 cpu with Delta tp04 hmi through rs232 port. I tried through 1747cp3 cable directly but can not communicate...
942