cblarsen
Member
Ok i work a a plant with multiple pc workstations(32 bit windows 7 or xp pro) running rslogix5 v7.40.00. With 20 differant processors I just got through setting everything up with factory talk activation with a server cliant situation that all went smooth. Now all the workstations grab a the program from a server (same file for all) and they open up off line fine but sometimes when you go online it looks like it is about to connect then rslogix5.exe crashes and shuts down. The only way i have found to get around this is to open off line program>>export ASCII database>>>then go "online now" without documentation then re-import the database . then we are connected and i save back to original file on server and connects fine after that . Any ideas? Here is a instruction sheet i made to put on the workstation for our E&I techs to work around if they have the problem