RSView ME Go To screen triggered from PLC

shilok

Member
Join Date
Jul 2007
Location
USA
Posts
28
Is it possible to trigger screen change with bit from PLC.

In Panel Builder you can do this by setting the control tag bit,
but I can’t find this function in RSView ME.

I’m using Panelview Plus 600 and CompactLogix L32E and/or Micrologix 1100.

Thank you
 
shilok said:
Is it possible to trigger screen change with bit from PLC.

In Panel Builder you can do this by setting the control tag bit,
but I can’t find this function in RSView ME.

I’m using Panelview Plus 600 and CompactLogix L32E and/or Micrologix 1100.

Thank you

Use the Remote Display Control, a non zero makes the PV+ jump to that screen. Each display must have a number assigned to it:


global_conn.jpg



display_num.jpg
 

Similar Topics

Hi. We have RSView 32 Ver. 7.50 We have been using our SCADA for several years now and had no real issues. Recently I build a new screen and...
Replies
0
Views
1,726
Hi all. I am about 6 months out of trade school and new to RSView ME. We design a HMI screen with a resolution of 1920x1080 for use on a 55"...
Replies
10
Views
5,517
Hello All,I am facing a problem these days regarding my scada screen...Actually the scada is Rockwell RS View 32 in which one graphical screen is...
Replies
3
Views
1,827
Hello, I need to create a pop-up screen (faceplate) for motors in RSView 32 Version 7.50, which includes start/stop push buttons, motor status...
Replies
0
Views
1,614
Does anybody know how to automatically switch screens for a panel-view application triggered on an alarm? For example automatically jump to the...
Replies
1
Views
2,271
Back
Top Bottom