RSView32 and S7-300
tulip
Oct 2005
ist
236
Hello ,Our customer has got a system that RSView32 and S7-300 Plc communicating on OPC server.Problem is communication is not working.I checked QuickStart_PFB MPI/S7 comm with Siemens S7-300 and S7-400 PLC.I run monpfb.exe (profibus monitor) program under applicom 3.8 and all of them seems good.When I looked VisuCYC window (user&system selected from 1 to 255)this window is blank that is no status.I checked s7-300 side that is MPI,DP address and protocols are okay.What is needed for communication between these two systems?Thanks is advance...
Tulip,
In your RSView32 System menu, check your Channel and Node settings. You must have valid entries in each box in order for RSView to communicate with your S7-300 PLC. Sometimes these settings get deleted or changed when the RSView program is moved or copied to a different computer.
What Lancie says
Also you may see an entry in the activity log that may be of help to you and / or to us.
If you are still having problems, could you tell us if this is an existing connection that stopped working, or a new one that has never worked, also what OPC driver you are using
Is it Profibus or is it MPI ?
What CPU is it exactly ?
What port is connected to on the CPU ?
Can you connect to the CPU from STEP7 ?
Use an OPC Test Client to see if it is possible to connect via the OPC Server.
cpu is 315-2 DP(6ES7315-2AG10-0AB0).MPI port connected to RSView side.And PCU1500S7 protocol selected at RSView side.Is it true?.
Yes I can connect to the Cpu from S7.When I looked to VISUCYC window.This window is blank!That is fnct status,board,channel,fnct,equip,period,protocol fnct,DB var...etc is not seeing!
I'm importing an RSView32 project into FTView SE. I'm using Legacy Tag Database Conversion on a virtual machine with Windows XP, I did the first...
391
Hi everybody, I have a rsview32 application, when I try to run it it loads upto 80% system settings and the crashes saying Rsview32 Project...
1,924
Hi Guys I'm having trouble assigning a tag to an activex label on a Multipage Tab. I can assign the tag to an active x label on a normal display...
608
I have followed the procedure below to convert RSView32 project to FactoryTalk View...
1,450
I have converted RSV32 to FTVSE Distributed. pretty straightforward... I cant seem to figure out how or find any documentation to migrate RSV32...
2,314