S5 115U CPU943B ( how many analog can fit it )
teh
Supporting Member
Nov 2002
140
Dear Folks,
I have a S5 115U CPU 943B in the plant running now,
with 3 A.I module 1 A.O module and several digital input and
output module and IM306 as well. The Center rack for all analog and
expansion rack for all DI and DO module.
The Arrangement of the Analog Module is just beside the CPU and CP
module .. 3 analog input ( 460-7LA12 ) following with the analog
output a analog output(470-7LC13). so i still have 2 spare empty
slot for future expansion. Can i used this 2 spare slot for analog
module? if can what is the address is should assignt?
Regards
jep!
check the rack for adressing.
If the cards are freely configuratable then adress them starting after the last ai -card or ao-card
Hi
One of the reasons for empty racks may be rack power supply limitation. You should check the specification sheet of cards and power supply and calculate that you have enough power for new cards.
If you haven't IM306 the analog address of the cards in the main rack started at 128 and the next analog cards became 128+32=160 and the next 192 and the 4th card got the address 192+32=224 and you can't place other analog cards on the rack because the nextc ard address exceed the limitation of 255. But when you have IM you can place the address of the cards with a distance of +16. So you should check the IM and user program.
My experience relate to other CPU models and may be not correct for your models.
Regards,
B.Najafabadipour
In S-115u cpu943b plc i removed eprom & battery then i done the overall reset , after overall reset , i put the switch in run mode (only with...
2,785
Hello friends I have a plc siemens S5 115u cpu 943 B machine was runing smoothly and stopped for break ,but when restarted the following...
8,855
Hello Dear, I am using a PLC SIMATIC S5 115U CPU 943B my problem that there is no output on CPU (943 B) ⚫️RUN STOP 🔘RUN 🔘STOP 🔘QVZ 🔘ZYK...
2,459
I have a S5-115U, 941B.... In OB1, I can see some block calls Like JU PB16, JU PB17 and so on.... But in the Directory I don't see these blocks at...
44
10,770
I did this once before but it was about 30 years ago I just tried it on a plc this morning and,when i fitted the eeprom and downloaded the...
2,157