I have the above CPU. I need to check if the onboard I/O are working. I am viewing it on line with Step 5. I have a manual for it, it has eight AI IW40...IW54, 0 - 10V, and a Analog output QW40 0 - 10V. I can drive a value to the output which I have tested with a meter. I want to use that output to drive the analogue inputs to test them. I have the pin out of the connector however when I connect the output to any of the inputs, the input value stays at KH=0000. Any ideas?
How do you connect? 1-14 and 9-15?
Do you still measure the same V?
I don't remember if one could change the IO-byte numbers in the MASK-DB. Could you check?
Kalle
I'm very new to S5 so I don't know about Mask DB. Using a multimeter I have toned out between pins 9, 11, and 15 so I think that they are linked together inside the CPU. Is it posible that the analogue out cannot source enough current to drive the analogue In?
Hi All,
I found my mistake. I was using viewing IW 40 instead of PW 40 in the Status variable. Using PW I can see that I getting values when I apply a voltage.
Thanks for your help.
Hi!
The MASK DB is probably called DB1 in your manual, and it is a setup interface to the operative system. If you aren't aware of the importance of this DB, it is wise to spend some minutes with the manual.
I only found the manual in German language, and I see one of the codes is about copying the PW into IW. The default is 0 (no copying) by entering OBA: AI 8 all 8 channels will be copied (I hope ;)). The CPU must be restarted after a change.
Kalle
Yes, DB1 is important for various settings.
You can also use FB250 and FB251 (if I remember the FB-numbers correct). They are onboard-FB's and are used to scale analog in- and outputs.
I m new in STEP 5 and i need help I have problem with the onboard's analog output 4-20mA, i want to forced it to see if it work or not but i...
2,017
I have a system with this PLC and there are 8 analog input devices connected to the onboard A/I terminals. In the program, I can only find PW40...
2,961
I would like to know if it is possible to read from an analog sensor 0-5 V with an analog module input of a s5-95u. I sow in the manual that this...
2,213
I am new to this forum and would need your help. I am looking for the Modbus FBs for the S5 95U for communication with the CP521. These FBs...
32
Hi there! This is something so old and having machine with it....... Last time unit was powered around 3yr ago and it did not work since than...
280