S7-1200 to redlion
Jezz
Dec 2002
Kendal
399
Hi All,
quick question I got a S7-1200 talking to a redlion G310, and I could do with being able to set some timer values on The S7-1200 from the screen is there an easy way to do this ?
I'm using Siemens S7 TCP/IP Master with TIA S7 Tag Import to import the tags I know that doesn't support time variables
I don't know Siemens PLCs at all, but I would think you could work around the problem by making use of the tag types that are supported with some PLC logic to copy the values to and from the actual timer addresses.
This is my standard practice for A/B PLCs anyway. I block off a group of integers and floats exclusively for use with the HMI which also makes for more efficient communications.
Thats what I was thinking , I'm new to the siemens but I was hoping there might be a easy work around
Are you using standard timers? Or the legacy S7 (not sure if that is possible..)
Try to declare the tags as DINT and set time at ms resolution.
The IEC timers use mSecs as standard resolution.
Also, see if the "optimized" "non-optimized" DB setup makes a difference if you do use DB's.
Hello, Anybody having sample program for the Micrologix 1200 and Redlion HMI using PM02 cable of Allen Bradley. Requesting you to share for the...
2,477
Setup: 1762L24BXBR SER C REV B FRN 12 RedLion G306A000 I'm talking to the RedLion DF1 Full Duplex through the Prog/HMI Port on the ML1200. My...
3,388
Does anybody have G3 series hmi and Micrologix 1200 communication diagram with cable details. and if anybody have the sample program then please...
4,297
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
255
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
82
