S7 200 pid
Some one
Jun 2020
Egypt
Hi every body
I am using pid block to control temperature through a Contactor(on /off) control
The problem :eek:utput is very fast pulses which is not good for the Contactor
What is the proper p, i, d values or is there a simple way to get it
By the way
Auto tune option takes much time and never ends with me
Umm, a PID output is analog, and a contactor is a discrete output.
So I expect you are using PWM; if so, try lengthening the duration of the PWM cycle to tens of seconds or perhaps several minutes.
Even that seems like a bad idea though. A simple bang-bang thermostat control to maintain the temperature in a band around the target temperature would be better, I expect.
You could use a timer and have the PID output determine the about of time, of the timer cycle, the contactor is energized. Start at something line 100 secs.
If PID output is 45, contactor is on for 45 sec, off for 55. If PID is 10, then on for 10 off for 90. You will have to determine the best timer cycle.
Hello all, I have set up a PID loop which works fine except it is a bit slow during the startup. I wish that it would reach near the setpoint...
1,836
I am using pid for temperature control on s7 200, cpu224 i/o module 231 and 232, 1.i am using ac0(memory) for giving set point values to pid,i try...
2,363
how can i use pid+pwm to control brightness of the ac light
2,246
Hello everyone, this is my tutorial for using PID function on S7-1200. Hope you guy like it. https://www.youtube.com/watch?v=INB6_7SqeOg
1,639
Hello everyone, I'm new in using plc software. I want to set a parameter for my centrifugal pump using an i/p from PID block so that the range of...
1,285