Hello
S7-200 CPU 224 CN is installed and SM31.7 is used for data write to EEPROM
Now I have uploaded the program from CPU 224CN and downloaded it to CPU 224 standard
problem is that when I set SM31.7 then it does not go back to 0 state and remains ON
what may be the reason?
waiting
Hello
According to the manual, SM31.7 goes to zero automatically after writing values
In Old cpu 224 cn , this function is working properly. When I set it, it becomes 0 automatically
But in cpu 224, it is not working. When i set it to 1, it remains 1
Please suggest solution
So it looks ok - I would suggest you go online and check each network where SM31.7 occurs to see if eg. M18.5 / M18.6 / V2000.4 etc are being "re-triggered" in the program?
M18.5 M18.6 etc are triggered from hmi
So there is no chance of being triggered inside plc
Moreover, same plc program works fine with old cpu 224 cn
Have you been online and checked?
What is the status of SM0.0
What is the value in SMW22
Failing this then the save function has not "finished" - (maybe a corrupt EEProm ? DB)?
I will check the status of SM0.0 and value of SMW22
so if it seems that the issue is due to some corrupt EEPROM then what is the solution?
Hello, I have a question about an encoder that has absolute measurement. Specifically, it's the Lika SMA5, which I would like to connect...
58
34
Hi. I have a 222 CPU. I need to recover the program from the eeprom memory. Is it possible?
122
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
283
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
99