S7 300 Instance DB Time stamp error
M_N
Oct 2009
WLKP
When opening instance DB I am receiving message:
"Time stamp of the FB or SFB for symbol XXX in FB101 is more recent than the time stamp of the logic block interface"
The problem is I've checked time stamps and they seem OK.
I also used "Check block consistency" and compiled everything without any errors.
Any sugestion? please help...
Regards
If you have compiled everything, then all the timestamps have also been updated. Download everything again, so that you have the same timestamps in the offline and online projects.
Try this...
Open the function that calls the FB.
- Try to save the function. If you get an error message about a time stamp conflict, you can select "File -> Check and update accesses".
- OR, select the function and select "Edit -> Block call -> update".
Plc s7300 cpu 312c
I have a PLC S7300 CPU 312C including 7 modules. But it have broken Module 1,2,3,4 (SM331; AI8 x RTD ; 311 - 7PF01 - 0AB0. SF light of its light. Sill another modules function normally. I DO NOT UNDERSTAND ANY MATTER WHAT HAPPENS. CPU still works great.PLS help me.
Thanks:geek:
Thanks:geek:
Perhaps it would have been better to start a new topic?
However if you have the software connect and check the diagnostics.
Thanks:geek:
Hello vancanh2000;
Every analog module manufactured by Siemens requires external power; lack of 24V power would be my first reflex explanation of the SF signal on your modules.
See the attached connection doccument for the 6ES7 331-7PF01-0AB0 modules; check that you have 24V DC at pins 21 (L+) and 40 (M).
If this connection is properly done, then check the diagnostic buffer of the modules and the CPU (use the HWConfig editor, go Online with the PLC, and double-click on each icon marked with a red slash, indicating failure).
Hope this helps,
Daniel Chartier
Hello all, Newbie in Siemens, I want to ask if there will be any issue when I download the instance datablock of a certain Function block? Also...
4,453
Hello, Using LAD, how can I generate an array of 50 numbers and then calculate an average of them? I don't know how to define an array as a...
29
11,507
What determines if a FB can be used as a multi instance? According to Berger "Prerequisite is that both the calling function block and the called...
5,859
Is there any way to initialize variables in an Instance DB? Example: In FB(X) I am using multiple instances of FB(Y). The Instance DB for FB(X)...
6,933