S7 300 scan times
Chris Taylor
Feb 2011
Canterbury
257
Morning
I don't have any experience with Siemens PLCs but I’m being told that a PLC with about 200, I/O, some remote, can process an input and operate a relay output in less than 10ms. Just standard input and output cards
Any thoughts? it’s for electrical protection and I’d usually hard wire and use the PLC for indication but it’s not my design, but I am being asked what I think.
Chris
What do you mean with 'electrical protection'?
Depending on the size of the program, which S7-300 CPU you use, it should be possible. If you just plonk it in the main program.
If you use an interrupt input, it'll be waaaaaaay faster.
Jeebs
By "electrical protection" I mean, to open a set of breakers to prevent danger to persons and equiptment.
basicaly a proection relay operates and opens a local breaker and that is hard-wired, it is also required to isolate four other breakers and the designer has opted to use a S7 300 PLC to distrubute that operation
Chris
Hello Everyone! As the title suggests, i would like to know how to program a "First Scan Bit" in S7-300 PLC CPU314. I made a sequence with 3...
3,176
Hey guys, Sorry if this is only a little PLC related, but has anyone had experience with this type of scanner before? We have an RS-232 setup...
1,643
Hi all, I probably have some short questions for you. I'm trying to understand timers and the Siemens operating system in more detail...
12,362
Hi all, I'd like realize a function to measure the scan time of the single FB or PB program block, not total CPU program scan time. I think to...
4,347
Hi Experts, Here is the problem, a HMI is communicating with a S7-300 system over an ethernet connection (using ISO TCP/IP Protocol). The scan...
7,683