Hi
I am writing program for Siemens plc S7 315-2DP.
I have got myself familiar with the software Simatic Manager.
Problem is all the drives are connected to PLC by prfibus, so if i want to change the speed then at what particular address i need to adrress the "speed output"?
Regards
Manmeet
The speed address is control word 2 of the drive, if you went with the default address's assigned by Simatic manager, then the address for control word 1 is probably PQW520, that means control word 2 will be PQW522.
Paul
s7315-2p to profibus
hi PLucas
So many thanx
The default address of DP is 2047,as assigned by the Simatic Manager.I connected masterdrive CB1 to prfibus havin diagnostic address of 2046.
Then what will be the speed address,trip alarm address and start/stop address of this drive
This will definately solve my problem
regards
manmeet
The address that you qouted is the DP diagnostics address, it is not the PQW and PIW address's of the drives.
Open up the hardware configurator and select each drive that is 'hanging' off your DP master system, there you will see the address's assigned to the drive, these will be the address's that you need to read and write to the drive.
In the download section of this site, I think it was JRW who has posted an example of communications to a masterdrive, this should give you some pointers on how to solve your problem.
Paul
I see you posted a picture while I was typing this reply, highlight the drive and read the address's assigned in there.
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
170
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
69
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
29
755
Hi We were having a few power cuts and the CPU would not work. I had to reset the memory and he CPU would read from the memory card and start...
3,178
Hi! I have never cross this kind of problem.. I have kind of working program on 315-2dp cpu. Program has been working nearly 20 years like this...
2,429