S7 400 CP 443 Redundancy

teh

Supporting Member
Join Date
Nov 2002
Posts
140
Folks,

I have a S7400 PLC with a CP 443 and link with a HMI software.

Is that possible that if i added another CP 443 as redundant

to HMI communication?

Regards
 
Yes, it is possible to communicate with S7 PLC via several links at the same time even from one HMI.
But if you have one PLC and only one HMI station, you are not on the right way...
 
The existing CP443(ethernet) have connected to HMI, we just suggest
add another cp443 ( ethenet) as standby comm. What we want is, once

the existing CP 443 was down , the HMI will automatically poll the

data from second cp443.

Mr Geogoyg, what do you mean by not the right way...

Best Regards
 
Why do you need redundancy between the HMI and the PLC?

The redundancy you are specifying only covers the CP card itself (which should be very resiliant) and the ethernet cable, so I would presume you would run the two cables a totally different route, as cable redundancy is installed to protect against damage to cable, which is normally caused by something cutting through it, so running them together would be self defeating.

But why make such redundancy? Redundancy is normally to protect the process, nice to have redundancy to the HMI but in most cases the HMI can be overidden by the tech's to get things moving. Its more common to have redundancy for the PLC and the process I/O.

Perhaps that is what gregoryg was referring to?
 
Yes Peter it is what i tried to say.
But if redundancy in HMI is needed than the best solution is to use two HMI's. They should be connected through independent links to the PLC and (of course i they are capable to) each one of them can use another HMI as backup path for connection to PLC (something similar to data gateway).
 
Last edited:

Similar Topics

I am troubleshooting the setup of UDP broadcast receiving on a CP443-1 CP card. The telegrams appear in WireShark with IP 192.168.1.255 Port 7551...
Replies
6
Views
2,322
Hi I have a system where essentially i am connecting an HMI via a switch to the CP443 card. I've set an IP address in the PLC end and an IP...
Replies
4
Views
1,574
hi to all, have anyone tried to communicate Schneider PM800 to a ML1400 through rs485? i am having an issue with it just receiving message...
Replies
1
Views
56
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
Replies
3
Views
119
I HAVE B&R POWEL PANEL 400 HMI. THE ISSUE IS HMI NOT BOOTING, DISPLY SHOWING CONTIUESLY (ATTEMPTING TO A BOOT HARD DRIVE....)
Replies
1
Views
77
Back
Top Bottom