s7 and scada

tulip

Member
Join Date
Oct 2005
Location
ist
Posts
236
I want a project with S7-300 Plc including also Scada(WinCC or Winflexible).I investigate optimal cost.What I need for communication between plc and pc ( hardware and software)? .I have 225 DI,100 DQ
Thanks in advance.....
 
One offer came.
CP343-1 card for S7-300 315-2 DP Plc 86GK7342-5DA02-0XE0)
1024 tag WinCC ( 6AV6381-1BP06-0AX0)
CP5613 card for PC (6GK1561-3AA00)
Driver ( 6GK1713-5CB61-3AA0)
is it optimal cost?
 
If the communication is TCP/IP and not ISO, you don´t need the CP 5613 because you can use the ethernet card in your PC and the CP343-1 can be the "Lean" model. This way you ca save lots of money (1500€).
 
Take a look at SIMATIC S7-mEC:
WinXP Embedded
Soft Controller - WinAC (functions of S300 series)
Works with WinCC Flexible too.
You will save on:
OPC,
Lean Ethernet card,
PC system block,
Windows XP.
 
A 315-2DP is a bit too small for a project with 225DI/100DQ.
Exchange the 315-2DP + CP343-1 for a 315-2PN/DP. It has more memory and the integral PN port is also faster. It is still a bit on small side, but at least better than 315-2DP. All in all also cheaper.

A regular Ethernet port in a regular PC will do.
So dump the CP5613 card.

For WinCC you need an RC license, and maybe an RT license. They are both very expensive. If you dont need all the bells and whistles of WinCC, then WinCC Flex RT is much much cheaper.
You will need WinCC Flex advanced + WinCC Flex RT 512 or 2048 tags + WinCC Flex archives or WinCC Flex recipes or WinCC Flex archives+recipes.
You possibly also need Simatic Softnet Lean.
With all this it is still far far less expensive than WinCC.

Spend some of the money saved on a good quality IPC for the Flex RT.

I would not chose the S7-mEC if you are a beginner with S7, or if Profibus DP is part of the project.
 

Similar Topics

Hello, im quite new and still learning. I would like to ask is it possible for FATEK PLC to read data value more than 16k? I'm trying to move my...
Replies
0
Views
88
Hello, the system we use is Scada 7.5 series. We have usb key activ now we need additional key to make the system work, how do we solve this...
Replies
0
Views
111
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
90
Hello guys please I want experience with this I am currently working on a scada project using FTView SE and I have an Ethernet IP local area...
Replies
0
Views
64
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
138
Back
Top Bottom