Dear frz, i got a serious issue on handling PLC. I had a program downloaded(FULL DOWNLOAD) onto the CPU. After the program execution, entire SYSTEM- PLC, I/O MODULES completely powers off. Even with the input supply to the PLC still active!!! pls help me out!!!
 
First you need an electrician with a multimeter.

Check the grounding and the M (0V) -connections.

Disconnect all equipment and reconnect one after one unit utill the failure occurs.

If the failure occurs when you restart the PLC, there could be a short one or more of your outputs.

Kalle
 
Last edited:
Do you use a Siemens S7 supply? If it is shorted you will probably hear some noise (ticking) from it..

Still the same problem if you disconnect all front connectors but leave input to CPU?
 
Did you do a clear/reset or clear the MMC before you downloaded?

Do you know the code you downloaded is 'good'

Did you download the correct hardware configuration

Is the CPU run light green? Stop light red?

Check module information -> stack report if stop light is red
 

Similar Topics

How can I integrate my S7-300 Simatic with the IFM AS-i Master AC1335 and its slave IOs, such as 2411 and Airbox 2041, into Simatic Manager?
Replies
0
Views
121
Hello everyone, One of our machine we use Siemens Cpu315-2dp. And this cpu communicate with 4 Lenze servo drives series 9300 via profibus. Also...
Replies
0
Views
184
Hi guys, I'm having problems converting WinAC (WinLC RTF F application) to S7 300 project based on CPU 319F-3PN or S7 400/416F-3PN. The problem is...
Replies
0
Views
619
Hi Any one here please helpmein simulation of s7 300 plc program with factory io. how to connect. plcsim 5 doesnot have option of s7 300 ..:
Replies
2
Views
1,014
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
Replies
2
Views
1,071
Back
Top Bottom