So I am wondering say you have the following circuits. If you have a safty controller that outputs to a single DPDT Standard relay that controls to E-Stop inputs into another device. Isn't that safer than using a single DPDT Force Guided Relay since if the force guided gets welded on one contact they all are stuck closed?
Now if you 2 force guided relays and use the seconds set of contacts in a NC configuration to the EDM of the safety controller this would obviously be safer correct?
See attached Drawings.
Now if you 2 force guided relays and use the seconds set of contacts in a NC configuration to the EDM of the safety controller this would obviously be safer correct?