Safey issue with motors & VFDs

rdrast is correct in his assessment of the problem with the instantaneous and time delayed safety outputs.

What is being described here is referred to as a Category 1 stop as per NFPA 79 (section 9.2.2, 2002 edition). This is a controlled stop, where power is being used to control the stopping action, then having power removed after the safe stopping of the system.

I also agree with rdrast that I never put equipment in the field that does not have an isolation contactor between the drive and the motor. The only way that I would not do that is if the drive manufacturer can supply documentation indicating the drive will operate at a level of safety without the isolation contactor that satisfies your risk assessment. (Do you have one of those?)

Of course, with a 10 second wind down, I do not see a way around a solenoid locking safety switch (power to open, prefferably). The time delay output on the safety circuit is good, but a zero speed detector is better. This will be more reliable over the long haul.

Using a brake motor for this application is not the best idea from my expereince. I typically try to use brake motors for "holding" loads, not stopping them. Using them to stop the load will significantly reduce the longevity of the motor (also braking time will vary, see note above). If you are anticipating this happening only ocassionally, then it probably isn't a problem. If this is something that is going to happen more frequently, then you may need to consider the longevity of the system. Additionally, in some applications you want the motor to spin freely with the power off (like spindle applications, so that you can tram stuff). With a brake motor, this is more difficult.
 

Similar Topics

I want to communicate my Q series PLC with Factory IO using GX works 2 software, I want to use modbus as server and the ips are as follows plc...
Replies
0
Views
13
Hi all, I'm new and i'd like to request some help please I cannot open those PVA files with panelbuilder32 so can anyone help me? Thanks in...
Replies
2
Views
22
I am kind of new to GE products, but we have several in my area. I made a minor logic change and it verified good, but when I tried to download I...
Replies
5
Views
40
Hello all, I am currently facing a problem with a Pro-Face HMI PS5000 project file download. I have tried using GP-ProEX SP1 (4.09.350) and...
Replies
0
Views
26
Hi there, Throughout testing I have made small changes and tested them on PLC sim. I don't have the S7-1200 or any hardware yet so have just been...
Replies
2
Views
72
Back
Top Bottom