scaling on SLC5/03
brian1
Feb 2004
I am trying to scale a value to read in Eng.units. I am applying 4 - 20mA into an analog card with the counts being 3277 - 16384. I ruined my brain trying to figure out the SCL function with no luck and couldn't figure out the tag scaling on the PanelView550 either so I thought I'd do it in the logic and just display the integer value on the display. I don't usually do the programming around here so I'm a little rusty on the scaling math. In short I want to take my 4 to 20 mA and display it as 0 to 100 PSI. If anyone can give me a clue I'll be forever grateful. God bless you.
Brian
On a 5/03 (or any A-B processor where it is available) I use the Scale With Parameters (SCP) function - it is easier to set up and modify.
In this example I have the full scale value stored in regiser N7:82. You can use a constant like 100 or 1000, but I like to be able to adjust the scaling from the operator interface in case the transmitters is replaced some day. Note that the 6242 and 31208 values are for an MicroLogix 1200 - your values should be used as appropriate. For most 5/03 applications I set up the card for engineering units, with 4000 to 20000 as 4-20 mA, but that isn't necessary.
I like to use a data file for input min, input max, and scaled min as well as scaled max so that that versatility is there for all the parameters.
(( Raw counts - 3277)/ 13107)*100)= Eng. units
Although above statement is mathematically correct,
I don't think it would provide proper result.
Reason is that after dividing by 13107 you would get
maximum 1.250019 which in integer world would be
simply 1. After multiplication by 100 your reading
would be either 0 or 100psi which is probably not
exactly what you wanted.
You could try using floating point math to get
correct result or simply divide by 131.
This would mean very very small error (0.053%)
but the result would be 0-100psi.
EngUnits=(Raw counts - 3277)/131
When you are scaling anlog input to an integer value, you have to foresee that the input exceeds 4-20mA.
When the input signal is outside 4-20mA, you have to think how the program react.
In Tom Jenkins demonstration of the SCP instruction, the destination value is scaled, but not limited between 0 and the value of integer N7:82 - in this case 320.
So an input value of 3.4mA (which is a typical output from a sensor when it is in error - another error signal is typical 21mA) will result in a destination value of less than 0.
If you have limited your panel to display values between 0-100, the value is then out of range and a series of asterics (*) will be displayed.
To avoid this situation, use GRT and LES in combination with MOV.
(LES N7:0 0 MOV 0 N7:0, meaning; if N7:0 is less than 0, then move the value 0 into N7:0). If you do this, you can at the same time set a flag to display an error message.
I have everything set up for vibration monitoring with the code in Controllogix 5000. The thing is that I am not able to read values SCADA in mm/s...
28
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
195
I want to measure the tank level and get the sensor output to the PLC. Below are the details : Tank Height =0 - 3m, the sensor is stalled 0,2m...
661
393
I know nothing about simaticnet OPC server. I do know Kepware. I would only ever scale raw to engineering in the PLC, but it is possible to scale...
229