SCP help with ML1100
gimmephone
Mar 2005
Windsor, Ontario
34
This may seem like a very stupid question to you guys but I am a bit stuck with this. I was playing with my ML1100 and trying to scale an input signal to an input voltage between 0-10 to 0-10000.
A screenshot follows.....
First, my question is why is I:0.4 shown as Analog Input0? Does the PLC automatically place a 16-bit result here based on the analog input value (0-1023)?? I ran this code and values of my output seem to change...I will get a better idea tomorrow when I try it out with a variable power supply. Can anyone tell me on the line after where I chose Input inside the SCF instruction as I:0.4, why does a 5 show up and correspondingly a 49 as my output value? Does this me that an input=Common is scaled to 49?
I have worked a lot with Modicon and AB to me seems like hell right now o_Oo_Oo_O!!
Thanks for the help
Twelve bit (with sign) is 0-1023
Sixteen bit (with sign) is 0-32676
I'm not sure about the ML1100 Input Cards, but if it's like the SLC 500, it's sixteen bit, so your SCP should use 0 low 32767 high.
The analog value is automatically put in the word file of the corresponding input.
Also, with your SCP as you have it now,
5/1023 * 10000 = 48.88 rounded to 49.
The 5 value probably means that your reference is floating slightly.
Dont you miss 30001 and 40001 right about now!!
I still cant get my head around all this I:0......but i am trying!
Good luck..
The analog input I:0.4 is an input on the base module, not on an expansion card. These are a relatively low resolution 0-10 volt input card, 10 bit which is 0-1023.
You can view the input radix in binary or decimal by changing the requested view.
The SCP instruction is just a linear relation. Your input is 5 of a maximum of 1023. (approx 1/200th) This corresponds to 49 of a maximum of 10000 (again approx 1/200th).
Change the N7:0 to F8:0 and make the scaled max = 10
This will give you a floating point value for the voltage applied to the analog input.
Regards Alan Case
Can you guys tell me if I set up these two SCP instructions correctly. Here are pictures of the instructions and the instrument specs.
6,440
Hello, I am replacing a pH probe that was determined to be bad in a waste water treatment system. I am replacing it with a 2-wire Aqua Metrix...
1,454
Hi I have a PLC 5/40E which passes speeds to a number of machines via rio. Currently there is no scaling and the machines use look up tables...
1,723
Rs logix 500 is version 12.00.00 and my SCP instruction is grayed outed. Can anyone help?
1,306
Hello everyone, I am using SLC 5/03 (1747-L531) CPU. My CPU gives an error. BATT led is active and it is always in solid red . Firstly I...
4,119
