I was assigned to calculate the pressure inside a tank which was filled by water,Once filled i have to calculate the pressure for any leak in tank... The psi range for the Ok product will be 25 to 30 psi..If less fail..
Now i need some guidance in how the pressure control will be mounted , how it will operate & feed back for plc will be 0-10v i will get psi value by scaling.
i can develop the programming part,,, no idea about the mechanical area ,operation,mounting type & how to do connections..Have to choose a AB product...
Thanks & Regards,
Nelliyan.G
for a start just put it all together with a valve and water from the tap.
now the dropratio should be less then ???
so measure the pressure and 1 minute later again now calc the drop.
It is not clear to me whether
- you want to control the level of the water by using head pressure measurement
- you want to control a blanketing atmosphere above the liquid
- the tank is open to the atmosphere or is a pressure vessel that is closed
Pressure control is done with an actuated valve, or maybe with a regulator, depending on what you're trying to do, which is not clear.
@danw
There will be a tank,,2 valve will be there,,first water will be filled by water till a overflow point.. once reached then that water valve will be closed ...then the pressure valve will be opened at 27 psi rate& then the leak will be checked for 15 minutes,,if any drop that tank is fail..
My prob is how to select a product for that,,,
Just use a standard valve with 27 PSI supplied to it and mount a pressure transducer in the tank to monitor pressure decay.
Hi, I'm working on Mitsubishi MR-J5-70A amplifier, and need some advice on selecting fuse size. Main power is 1ph 240VAC, and in the manual, it...
103
I am working on trying to create a an HMI program where the user can select a value from 1-25 and then enter a string, which will be placed into...
1,104
We had a servo motor feedback cable get damaged recently and we want to order a replacement. The current cable is a custom made cable, and we...
909
Not sure how to word the title but here's my scenario. We have a carriage that moves at high speed with an energy chain and the cable bends in a...
2,885
Hello plctalk, new guy here. I have an application that I'd like to present for your considered opinions so I can figure out what hardware I...
2,543