Serial Port on the Logix 5562 to RS-485
RetiQlum
Feb 2017
Arkansas
30
I have a 5562 that I need to attempt to connect to a RS-485 Emerson Drive. The issue I have is that I can't for the life of me find the pinout.
Also, is this possible without a converter? I remember needing to use an adapter with other PLCs. I need it to do Modbus-RTU. I will be getting the ProSoft (4 ports needed if you believe it) cards with the new PLC when it comes in, but I need to use this old one for the time being.
Thanks in advance.
I need 4 ports because there are 4 drive controllers. The response time for serial communications is too low. Of course if we just added the Ethernet/IP modules to the controllers would could save something like $8k per system these go into.
You will probably not be satisfied with the response time of the Modbus/RTU sample code for the 1756-L6x serial port, especially if you're daisy-chaining it to multiple devices.
How many read/write registers to you need to do per Emerson controller ?
If you just need to do a few, and you don't mind spending a little time experimenting with configuration, the GridConnect NET485 is the most cost-effective way to connect a handful of Modbus/RTU serial registers to a ControlLogix over Ethernet.
It only addresses one slave device, but it's $100 retail. And once you get the configuration file figured out, you just load it via TFTP and you're done.
Why don't you connect the drivers in a dasy-chain?
The response time will be an issue if you intend to control the speed using a PID from the controller. In similar configurations, I use the internal driver's PID and set the speed from the PLC. Of course, I don't know if that's possible in your application.
Hello. I am trying to establish communication between CompactLogix 1769-L32E and CompactLogix 1768-L43 using serial port but with DeviceNet (and...
2,763
Hello, I need to read a serial port. The serial port in question would be on a pressure gauge and would be read by a Logix 5000 CPU with a...
2,008
Hi all, i got some problem about i think some configuaration in mine micrologix1100. I try to write some string (ascii) via serial com to some...
2,272
Hi Guys, I'm trying to connect a non-brand LED display to the 1756-L63 ControlLogix. The display can communicate via RS232 (one direction), RS422...
2,115
Hi, I'm trying to send hex strings to a printer via the serial port of my micrologix 1500 but it is not working. I'm not getting any activity...
3,286