Servo holding brake question

ceilingwalker

Lifetime Supporting Member
Join Date
Mar 2010
Location
Phoenix, AZ
Posts
1,589
Hello all. I have retro-fit new servo amps and motors into an ancient machine. I am accustomed to using 24VDC from a switching PSU to energize and release a servo motor brake. On this unit, they feed the brake with a bridge rectifier, no filter. I am by no means an expert with servo systems so my question is, why would someone energize the holding brake this way? Thank you
 
Old School & Cheaper. The Servo Motor likely has a 24vdc brake. A small transformer and bridge should be cheaper than a full power supply. BUT, in today's market, with 1000's of cheap little power supplies being made, the power supply may actually win the cost + labor total.
 
Thanks guys. My only concern is the fact that it has no filter of any kind. I just don't want the ripple to wreck my brake coil. I guess as long as the mean voltage isn't allowed to drop too low, it won't notice a difference.
 

Similar Topics

I am installing a kinetix 5100 on a machine, driving a MPL servo, and it's my first time tuning a servo PID. I'm happy enough with the behavior of...
Replies
10
Views
215
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
Replies
10
Views
162
Hi guys, I need help with position control using a Veichi AC Servo Drive model SD600A1-T2-2R2. How do I know how many pulses for it to rotary 1...
Replies
3
Views
131
Hi, I'm working on Mitsubishi MR-J5-70A amplifier, and need some advice on selecting fuse size. Main power is 1ph 240VAC, and in the manual, it...
Replies
1
Views
109
Good morning, We've had an issue with a couple of servo valves and was wondering if anyone had seen anything similar. After a drop in pressure...
Replies
2
Views
127
Back
Top Bottom