SEW Movidrive N-Monitoring Fault
Rob S.
Sep 2008
Maryland
739
We have a SEW Movidrive driving a SEW KA67 DY90S/B/TF.
It is using it as a servo for a lifting device. It has 1 Up
Limit , 1 Down Limit and 1 Reference Switch in the middle.
We replaced the drive and we keep getting a N-Monitoring fault could someone explain what this fault is in more detail, because in the SEW manual it has a number of causes. I understand that I can turn this off at Par. 500 and 501.
It seems like it is related to " nMax is exceeded during torque control". Any ideas would be great,
Thanks,
Seems like your lifting device is actually trying to lower heavier stuff than it used to do...
Easiest thing to do: Try to increase deceleration and move the limit switches accordingly.
A bit harder: You could try to recalibrate the drive to the current situation; use the 'scope' function in the movitools software to examine where/when it goes wrong or what could be improved. There's a good chance the PID is overshooting in relation to the load.
I saw the same fault when I was trying to stop a motor too fast with a heavy load pushing it. Slow down the ramp and add an external resistor to reduce the energy the VSD has to dissipate during stopping.
Hi , I am trying to replace an old inverter with a new one and its giving me issues . Once the new one was installed , the S7-300 PLC started...
131
What does the 24V operation of sew inverter mean? I can't make the inverter starting the motor
479
Hello, I'm having trouble with our SEW Movidrive "MDX61B0075-2A3-4-0T" error code F14 and I want to go through the program using MOVITOOL...
1,384
Hi everybody, In my project , I want to implement a positioning control of a Servo motor and drive from SEW manufacturer. My PLC is S7-1511-1PN...
2,067
Hi all, I just had a SEW Movidrive VFD go out in my plant. Upon reinstallation and reconfiguring, I'm finding that some of the drive parameters...
3,039