sfb52 siemens simatic 300

steffa5

Member
Join Date
Jan 2009
Location
Lorsch
Posts
1
hi, i'm tryin 2 use the sfb52
what i wanna do is to read data acyclicly from index 84 slot 1.
it seems as if the sfb52 works and the busmontiring with profitrace shows that there is a acyclic communication with the device from which I wanna read the data, so far so good.
but the busmonitoring says that index 84 slot 0 is read, unfortuntely this is the wrong slot...
My questions is now is it possible to "tell" the function which slot i wanna to read (i couldn't find a parameter...) or is there any other function which should be used instead of sfb52?
thx
 
Yes, there is another programme block with similar purpose SFC59. But SFC59 has less of diagnostiс information then SFB52 has.

Does both of your devices support DP V1?

SFC59 and SFB52 are don't working over DP V0. For example CP342-5.
 

Similar Topics

Has anyone here had success with reading or writing parameters directly to a device using the SFB 52 or 53 blocks in TIA portal? My problem seems...
Replies
1
Views
6,086
Hi All, I wanna read diagnostic data from Profinet module and I try use function SFB52. I have problem during configuration this block, because I...
Replies
0
Views
2,336
S7-315 Master Sirius Softstarter 3RW44 Profibus DP slave I want to read DATA SET 95 ID NO: 603 "Number of starts motor right" DP...
Replies
4
Views
12,397
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
Replies
10
Views
162
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
Replies
0
Views
83
Back
Top Bottom