Siemens 1214C Series
mbowling
Nov 2013
cincinnati
Hi everybody.
This is my first post so let me know if i left any information out that is needed. I am having a problem with my siemens 1214C CPU. We updated our packaging machine to a new siemens 1214C. However the machine ran like a top for 12 hours and then the CPU and its attached cards would power down for a split second and then power back up. I hooked a scope meter up to the power going in to the cpu and cards, to find out there was no power loss going in to the plc. I changed out the PLC and changed the program to an older version that we have in another "working" machine. The problem can be hard to diagnose because everytime this happens i lose connection to the PLC. The problems happen intermittenly but do however happen at the start of the cycle when it does occur. If you could help it would be greatly appreciated. I have been beating my head against the wall for 3 days now.
Thank you.
Not a fan of part swapping but.... do you have another 1214C, this is assuming that the CPU you replaced with (and the old program) was a different type of PLC?
I have installed a lot of 1214 and 1212 and never had any issues (yet)
Hi everybody.
Thank you.
To me it sounds like a short circuit in an input/output signal/cable. Does the cpu have its own separate power supply?
Kalle
Either use Online & Diagnostics to view the PLC log for errors, or enable the Web Server and view it there. Best to set the clock to the right time first so that you can know what error relates to which event.
Hello all; I need to create a software program that is a stand-in for a PLC I/O card. My program will be controlling a coordinate measuring...
3,397
Hi All, I am trying to communicate siemens PLC with FESTO Servo & 3 Festo make Steppers on FHPP Modbus Protocol. Sometimes, I face Modbus...
1,367
Hello, My problem is i need to change a siemens S5 rig to a S7 1214c The only problem i have is 2 things: 1) On the S5-95u there is a 8x analog...
3,912
Hi! What is the way to convert the code from the Codesys code to the Tia Portal? Regards, WK
73
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
208