Siemens 2nd HMI connection to PLC not in project

JDCROCKETT724

Member
Join Date
Jun 2010
Location
Michigan
Posts
249
I have a TIA portal project with an HMI connected to the PLC in that project.

Is there a way to setup a connection to another 1500 PLC that is not in the project?
 
I have a TIA portal project with an HMI connected to the PLC in that project.

Is there a way to setup a connection to another 1500 PLC that is not in the project?


You use a device proxy. Look up Inter Project Engineering (IPE) in the help. Essentially, it creates an export file of all the 1500 information that the other project can connect to.




Alternately, you can use the S7-300 driver, with non-optimized DBs.
 

Similar Topics

Hi, I have been looking on ebay for a while trying to find a good deal. Most are from overseas and i'm a little skeptical about purchasing them. I...
Replies
12
Views
2,157
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
Replies
0
Views
6
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
Replies
8
Views
96
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
2
Views
89
Hi all! Please inform me if i can make programing of the HMI SIEMENS IPC477D from TIA Portal software or not? I do not have WINCC software but...
Replies
0
Views
65
Back
Top Bottom