Siemens AG_RECV Buffer Issue

Rusty_K

Member
Join Date
Mar 2004
Location
Norway
Posts
73
Hey Guys!

I've run into a rather annoying little problem with the Siemens AG_RECV block (using a CP343-1) when trying to read data back from an RFID Reader.

It seems as though the NDR bit stays low until the entire buffer is full. At this point my received data will be in variable lengths so I cant really lock down my buffer size. Also, for some reason, if I try and set my buffer size to anything less than 130 Bytes if get a 80B1H error code meaning "Destination" area invalid.

Does anyone happend to have a work-around for this silly silly issue?

Ya just got to love those crazy cats at Siemens...

Cheers!

R.K.
 
Hi R.K.

I've run into similar problems also. I think this might help:

Link to Siemens forum

We solved the problems by always sending a same length message, from a server in this case.

Maitomies
 

Similar Topics

Can you please help me to choice the “best” solution for communication between CPU:s. I have following kind of system: I already have created S7...
Replies
6
Views
8,196
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
2
Views
57
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
7
Views
204
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
89
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
157
Back
Top Bottom